paragon said:
I had an install a couple weeks ago and I just realized that my installer didn't install a one of those 4-wide coax grounding connectors to connect the four coax cables to. He did run a grounding wire from the dish (compressed underneath a bolt) to my SWM8's grounding connector. The other SWM8 grounding connector is grounded at my electrical box.
Is this ok or should I call DirecTV and ask them to come out?
I would have D* come and install a coax ground block and bond this to the main electrical service ground (using a new clamp, 2 wires under the same ground clamp at the ground rod is not permitted).
If the coax ground block is over 20' from the main electrical service ground, a new 8' ground rod should be fully inserted into the ground at the ground block and bonded to the main electrical ground. This bonding is done to prevent a potential voltage difference b/w the two ground rods.
I don't have a SWM, but do these have a built in ground block?